Bob,

Either or. The original documents were designed for 13r but we have since
received clarification that the building could have been designated per unit
to be 13d. We would have to get the Engineer of record to revisit it
(Florida law) but it could be done easy enough.

The attic has always had a storage room with walls and a ceiling. We
actually calculated 4 heads and considered a closet due to the fact that it
had sheetrock walls and ceiling, but they have enlarged it and decided to
take the ceiling out so now the room is really an enclosed small exposed
attic with multiple slopes. 

I believe that we definitely need to put heads in the attic but the way I
see it we are now using SSU heads with steel pipe and the phrase "starting
over" would have HUGE economic impact on this job.

Roland?

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight
Sent: Friday, December 01, 2006 3:01 PM
To: [email protected]
Subject: RE: Attics in 13r and 13d

I remember this question from a couple of years back, and Roland gave an
answer something to the affect, that unless the attic is to be used for
habitation, it doesn't need sprinklered.  That is if you have a 13D system.
It sounds like that from your description.  So, I guess the question should
have first been asked, is this a 13D or 13R system?

Bob Knight

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Friday, December 01, 2006 1:46 PM
To: [email protected]
Subject: Attics in 13r and 13d


OK,

So what do you do when the builder decides to frame the attic at the end of
the job with pull down stair access for storage purposes after the pipe is
run and sized?

Exposed wood, sloped structure 6/12. If we have to use 13 with upright heads
there is absolutely no way the calcs will work for these 6 heads.

Thanks,
Greg McGahan



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to