I remember this question from a couple of years back, and Roland gave an
answer something to the affect, that unless the attic is to be used for
habitation, it doesn't need sprinklered.  That is if you have a 13D system.
It sounds like that from your description.  So, I guess the question should
have first been asked, is this a 13D or 13R system?

Bob Knight

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Friday, December 01, 2006 1:46 PM
To: [email protected]
Subject: Attics in 13r and 13d


OK,

So what do you do when the builder decides to frame the attic at the end of
the job with pull down stair access for storage purposes after the pipe is
run and sized?

Exposed wood, sloped structure 6/12. If we have to use 13 with upright heads
there is absolutely no way the calcs will work for these 6 heads.

Thanks,
Greg McGahan