Greg: If the building is code-classified so that it could be protected per either 13D or 13R, then the sprinklers in this storage space have to be classified (interpretively) as either within or outside of the dwelling unit. If it's a 13R design, I would say there's a pretty strong argument that these compartments are part of the dwelling unit - they can only be accessed from or egressed back through the dwelling, they are within the fire-rated envelope of the same dwelling, they're not in common areas or HOA-owned areas, etc. So I would say in that case that you can protect them with residential sprinklers and stay within the four-sprinkler design area at .05 - except for the roof slope. Can a flat or less-sloped ceiling be furred down?
If the AHJ is adamant that they're not buying that, let's compare the space to a garage. One could make the very reasonable argument that the hazard of such an area is no worse than a garage and 13R offers us an interesting guideline in 2002-6.7.3.3 (2007-6.8.3.3): The criteria for protecting a garage that is only accessible from a single dwelling is to use either QR or residential sprinklers at a density of .05. All of this is consistent with the line of reasoning that it's all more like a dwelling than not, so long as it's accessible only from that dwelling and within the same fire area (rated envelope). Steve Leyton Protection Design & Consulting The foregoing is the opinion of the writer alone, and does not necessarily represent the intent of the NFPA Technical Committee on Residential Sprinkler Systems, nor constitute a formal or informal interpretation of the standard. -----Original Message----- From: Greg McGahan [mailto:[EMAIL PROTECTED] Sent: Friday, December 01, 2006 1:13 PM To: [email protected] Subject: RE: Attics in 13r and 13d Bob, Either or. The original documents were designed for 13r but we have since received clarification that the building could have been designated per unit to be 13d. We would have to get the Engineer of record to revisit it (Florida law) but it could be done easy enough. The attic has always had a storage room with walls and a ceiling. We actually calculated 4 heads and considered a closet due to the fact that it had sheetrock walls and ceiling, but they have enlarged it and decided to take the ceiling out so now the room is really an enclosed small exposed attic with multiple slopes. I believe that we definitely need to put heads in the attic but the way I see it we are now using SSU heads with steel pipe and the phrase "starting over" would have HUGE economic impact on this job. Roland? Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight Sent: Friday, December 01, 2006 3:01 PM To: [email protected] Subject: RE: Attics in 13r and 13d I remember this question from a couple of years back, and Roland gave an answer something to the affect, that unless the attic is to be used for habitation, it doesn't need sprinklered. That is if you have a 13D system. It sounds like that from your description. So, I guess the question should have first been asked, is this a 13D or 13R system? Bob Knight -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Friday, December 01, 2006 1:46 PM To: [email protected] Subject: Attics in 13r and 13d OK, So what do you do when the builder decides to frame the attic at the end of the job with pull down stair access for storage purposes after the pipe is run and sized? Exposed wood, sloped structure 6/12. If we have to use 13 with upright heads there is absolutely no way the calcs will work for these 6 heads. Thanks, Greg McGahan _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum