Mario - I think to make the leap from water velocity in a sprinkler system
piping to anarchy and chaos might be pushing the ticket a tad.

As far as "For the same job if a contractor calculates the pipe with 20 fps
, other contractor calculates with 30 fps and another with 50 fps; the
contractor with 50 fps will win the bid.     Is that correct? is that fair?"
the answer is YES and YES.

The only way the design velocity will be reached is if all the sprinklers in
the design area operate and discharge.  Have you ever been to a fire scene
where the remote area sprinklers - all of them by the way - have actually
been the sprinklers which controlled or extinguished the fire?

>From what I have heard on here, fast velocity causes excess friction loss
and is self-regulating.  If you have data that shows a poor sprinkler system
response to a fire was caused by the velocity of the water, sharing that
data would convert many that do not share your passion at this time.  Until
then, adhering to all of the current requirements, and basing your design on
those requirements, should be considered admirable.

Garth

----- Original Message ----- 
From: <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Saturday, January 13, 2007 10:11 AM
Subject: Re: max velocity


> Mark,
> Several years  ago I wrote several e-mails to the Forum on this subject;
they may be in the Archives. In the past 20 fps was indicated in NFPA 13;
slowly thru the years that  20 fps  was taken out; if a limit is not given
then anarchy , chaos will happen. I have reviewed plans with 56 fps and the
contractor is right ,nfpa 13 says no limits in velocity. The statement about
good design , conservative design, prudent design is not read.
> For the same job if a contractor calculates the pipe with 20 fps , other
contractor calculates with 30 fps and another with 50 fps; the contractor
with 50 fps will win the bid.     Is that correct? is that fair?
> Mario Berrios,P.E.
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> To: [email protected]
> Sent: Wed, 10 Jan 2007 1:16 PM
> Subject: RE: max velocity
>
>
> Brilliant!
>
> It will take several Guinesses to get through this I'm sure.
>
> LMAO,
> Steve Leyton
> Protection Design & Consulting
>
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED]
> Sent: Wednesday, January 10, 2007 10:04 AM
> To: [email protected]
> Subject: RE: max velocity
>
> Because water faster than 20fps can quickly get out of control and drown
> people in nursing homes.  Slower water is less threatening.
>
> But seriously, why place a limit of 20?  There are times that through a
> particular section of pipe where the velocity may exceed that.  It makes
> little sense to have to increase a 5ft piece of pipe because the
> velocity in it may have hit 30fps.  You've got to use some common sense
> and good engineering judgment, balancing a practical design AND
> installation.
>
>
> Craig L. Prahl, CET
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [EMAIL PROTECTED]
> http://www.lg.com
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Mark
> Sornsin
> Sent: Wednesday, January 10, 2007 12:50 PM
> To: [email protected]
> Subject: RE: max velocity
>
> Mario:
>
> Given all that has been said on this forum, in addition to Roland's
> dissertation, I have to ask why the 20 fps limitation?
>
> If we engineers are going to require such a limitation, I believe we
> have to be ready to defend it. (this holds true to anything we write in
> our specifcations
>
> Mark A. Sornsin, PE
> Fire Protection Engineer
> Ulteig Engineers, Inc.
> Fargo, ND
> 701.280.8591
> [EMAIL PROTECTED]
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of
> [EMAIL PROTECTED]
> Sent: Wednesday, January 10, 2007 11:35 AM
> To: [email protected]
> Subject: Re: max velocity
>
> I recommend maximum 20 feet per second water velocity in fire sprinklers
> systems .
> Mario Berrios, P.E.
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> To: [email protected]
> Sent: Wed, 10 Jan 2007 11:44 AM
> Subject: RE: max velocity
>
>
> NFPA 13 does not stipulate a maximum limit on velocities; some
> insurances companies modify NFPA 13, such as FM, to restrict 20fps on
> gridded sprinkler systems.  I believe NFPA 15 does require velocities
> pressures.  Anyway, I was always taught that good engineering practices
> restrict velocities pressures to a maximum of 32 fps in branchline
> piping.
>
> Hope this helps.
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Ivan
> Cabrera
> Sent: Tuesday, January 09, 2007 4:58 PM
> To: [email protected]
> Subject: max velocity
>
> Would anyone be able to give me any info on the max velocity for
> sprinkler piping? If so, can you give me a code section it would be
> under?
>
>
>
> Thank you,
>
>
>
> Ivan Cabrera
>
> Fire Plans Examiner
>
> Town of Gilbert
>
> 90 E. Civic Center Drive
>
> Gilbert, AZ 85296
>
> ph 480-503-6957
>
> fax 480-497-4923
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> ________________________________________________________________________
> Check out the new AOL.  Most comprehensive set of free safety and
> security tools, free access to millions of high-quality videos from
> across the web, free AOL Mail and more.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> ________________________________________________________________________
> Check out the new AOL.  Most comprehensive set of free safety and security
tools, free access to millions of high-quality videos from across the web,
free AOL Mail and more.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to