>From NFPA 20: 11.1.3.2  Spark-ignited internal combustion engines shall
not be used.

Unless they have somehow created a compression-ignition propane engine,
such an arrangement is prohibited.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - work
Sent: Friday, February 16, 2007 9:39 AM
To: [email protected]
Subject: back-up power

I am working on a project where an electric fire pump (diesel not an 
option) and tank is the only source of water for the sprinkler 
system. The primary supply is the public utility and the back-up is 
to come from an on-site generator. The builder is proposing to use a 
propane-fired generator. I looked in NFPA 20 and 110 and didn't see 
anything saying this was a no-no. Is there a problem with this
arrangement?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 