Yes 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Tuesday, March 13, 2007 5:18 PM
To: [email protected]
Subject: Re: Small Room Rule

Seems like everyone is forgetting the square footage limitation. 225 sqft
max = 9-0 off one wall, 6-0 off one wall and 7-6 off two walls or any
configuration that does not exceed 9-0 off one wall, 7-6 off the other three
walls AND 225 sqft.

On 3/13/07, Brian Harris <[EMAIL PROTECTED]> wrote:
> That's the way I was taught, but if you look at A.8.6.3.2.4 (b,c,d) it 
> looks like you can only be 6'-0" off the wall if your 9'-0" in the same
direction.
>
>            Regards,
>               Brian Harris
> First Defense Fire Protection
>         Design Engineer
>    [EMAIL PROTECTED]
>            704.948.3506 phone
>            704.948.3507 fax
>
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Bill 
> Minkel
> Sent: Tuesday, March 13, 2007 4:53 PM
> To: [email protected]
> Subject: RE: Small Room Rule
>
> You can be 9' off any ONE wall and 7'-6 max. off any other 3
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Brian 
> Harris
> Sent: Tuesday, March 13, 2007 4:38 PM
> To: [email protected]
> Subject: RE: Small Room Rule
>
> Ed,
> Thanks, obviously there can be any combination of sizes that equal up 
> to 800 sq.ft. so those dim's can vary accordingly. One other question, 
> why when there's only one head can you be up to 9' off one wall and 
> still be 7'6 off the other (16'6" direction) but when there's 2 or 
> more heads the max you can be is 9'-0" & 6'-0"?
>
>
>               Brian Harris
> First Defense Fire Protection
>         Design Engineer
>    [EMAIL PROTECTED]
>            704.948.3506 phone
>            704.948.3507 fax
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of 
> Tambini, Ed
> Sent: Tuesday, March 13, 2007 4:17 PM
> To: [email protected]
> Subject: RE: Small Room Rule
>
> 30' x 26'-8 = 800 sq ft max size for small room It's what's left over 
> from the 2 7'-6 dims
>
> Ed
> Aero
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Brian 
> Harris
> Sent: Tuesday, March 13, 2007 12:42 PM
> To: [email protected]
> Subject: Small Room Rule
>
> Figure A.8.6.3.2.4.(d) shows an example of the small room rule with 
> (4) heads, where exactly does the 11'-8" between rows come from?
>
>
>
>            Regards,
>
>               Brian Harris
> First Defense Fire Protection
>         Design Engineer
>
>     <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED]
>            704.948.3506 phone
>            704.948.3507 fax
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>


--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to