OK, depending on room size, technically, considering max coverage, yes. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tambini, Ed Sent: Tuesday, March 13, 2007 5:04 PM To: [email protected] Subject: RE: Small Room Rule
Actually you can only be 7'-6 off 2 walls. In a single head situation for hydraulically calculated systems, 16'-6 * 13'-7½ = 225 sq ft max coverage for light hazard standard sprinklers. So it's 7'-6 off one wall and 6'-1½ off the other. Ed Aero -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel Sent: Tuesday, March 13, 2007 1:53 PM To: [email protected] Subject: RE: Small Room Rule You can be 9' off any ONE wall and 7'-6 max. off any other 3 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Tuesday, March 13, 2007 4:38 PM To: [email protected] Subject: RE: Small Room Rule Ed, Thanks, obviously there can be any combination of sizes that equal up to 800 sq.ft. so those dim's can vary accordingly. One other question, why when there's only one head can you be up to 9' off one wall and still be 7'6 off the other (16'6" direction) but when there's 2 or more heads the max you can be is 9'-0" & 6'-0"? Brian Harris First Defense Fire Protection Design Engineer [EMAIL PROTECTED] 704.948.3506 phone 704.948.3507 fax -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tambini, Ed Sent: Tuesday, March 13, 2007 4:17 PM To: [email protected] Subject: RE: Small Room Rule 30' x 26'-8 = 800 sq ft max size for small room It's what's left over from the 2 7'-6 dims Ed Aero -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Tuesday, March 13, 2007 12:42 PM To: [email protected] Subject: Small Room Rule Figure A.8.6.3.2.4.(d) shows an example of the small room rule with (4) heads, where exactly does the 11'-8" between rows come from? Regards, Brian Harris First Defense Fire Protection Design Engineer <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED] 704.948.3506 phone 704.948.3507 fax _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum