This is typical if IT and other "sparky's".

Inergen or any other gaseous system for a closet that size would be a
ridiculous waste of money.  

They can leave the head out if they can meet NFPA 13, 2002, 8.14.10
Electrical Equipment, and if their Underwriter agrees (if there is one).



Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Duross
Sent: Thursday, April 05, 2007 2:49 PM
To: SprinklerForum
Subject: Server Closet

I was wondering if I could get recommendations of advice to give a
client.
Their IT guy is bugging them about a head we put in a server closet.
It's just a 6' w x 3' deep closet with their rack and a little ductless
ac unit.
No raised floor, liebert or big ups equipment and certainly not sealed.
I offered high temp head but they're scared about water (wata).
Should I suggest total flooding inergen?  Low temp rate of rise heat
detector?
I have to have an exhaust system installed with inergen, right?
I think they'd have to enclose the closet to keep in the gas.

Thanks,

Tom Duross
Go Red Sox


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to