Unless of course IBC 904.2 Para. 2 applies, otherwise alternative automatic extinguishing systems are acceptable.
John Drucker -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Thursday, April 05, 2007 3:02 PM To: [email protected] Subject: Re: Server Closet Tom: We had the same issue recently. We provided a 360'F head located at the door access (4" off wall, with head guard) We had asked the IT guy at what temp was all his stuff fried anyway, and he said anything over 300'F and it all had to be replaced. Hence the 360'F head. Where it's located at the doorway it is protected from most possible damage by the lintel over the door and the guard is just incidental. Any small leak or drip would drop straight down and not on any equipment. If your dead set against a wet head, I think there are Intergin Balls out there for confined spaces, like boat engine rooms ect. Thom McMahon Firetech, Inc. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel: 970-879-7952 Fax: 970-879-7926 ----- Original Message ----- From: "Tom Duross" <[EMAIL PROTECTED]> To: "SprinklerForum" <[email protected]> Sent: Thursday, April 05, 2007 12:49 PM Subject: Server Closet >I was wondering if I could get recommendations of advice to give a client. > Their IT guy is bugging them about a head we put in a server closet. > It's just a 6' w x 3' deep closet with their rack and a little ductless ac > unit. > No raised floor, liebert or big ups equipment and certainly not sealed. > I offered high temp head but they're scared about water (wata). > Should I suggest total flooding inergen? Low temp rate of rise heat > detector? > I have to have an exhaust system installed with inergen, right? > I think they'd have to enclose the closet to keep in the gas. > > Thanks, > > Tom Duross > Go Red Sox > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)