Wandering into the wasteland, I'm guess it's a "double-interlocked
pre-action" system.
Just a thought.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
Tom Duross wrote:
DIPA??
In my best Sherman: "Gee Mr. Peabody, what's that?"
Tom
Sounds like they're concerned with water damage and not mission
continuity. I would recommend a DIPA system. Either way, it seems like
a lot of effort for one sprinkler.
Inergen would likely require pressure relief venting.
Ray Schmid
I was wondering if I could get recommendations of advice to give a
client.
Their IT guy is bugging them about a head we put in a server closet.
It's just a 6' w x 3' deep closet with their rack and a little ductless
ac
unit.
No raised floor, liebert or big ups equipment and certainly not sealed.
I offered high temp head but they're scared about water (wata).
Should I suggest total flooding inergen? Low temp rate of rise heat
detector?
I have to have an exhaust system installed with inergen, right?
I think they'd have to enclose the closet to keep in the gas.
Thanks,
Tom Duross
Go Red Sox
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)