A rain tight cabinet? I could see the thing costing 100K, they have a T1 and about 20 TB in data storage plus the stacks of ups's. I'll price out a preaction system and see how they respond. I'll also offer a dry head. I think there's just too much spaghetti wiring to contain it all.
Tom Enclose the server in a cabinet. John Drucker Fire Protection Subcode Official New Jersey I was wondering if I could get recommendations of advice to give a client. Their IT guy is bugging them about a head we put in a server closet. It's just a 6' w x 3' deep closet with their rack and a little ductless ac unit. No raised floor, liebert or big ups equipment and certainly not sealed. I offered high temp head but they're scared about water (wata). Should I suggest total flooding inergen? Low temp rate of rise heat detector? I have to have an exhaust system installed with inergen, right? I think they'd have to enclose the closet to keep in the gas. Thanks, Tom Duross Go Red Sox _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)