I got a set of lower pressure clappers from them and it only did it slightly. That was a few years ago. Did the gong start and stop too? Weird!
Tom Duross Go Red Sox -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Behalf Of John Drucker Sent: Monday, April 30, 2007 4:25 PM To: [email protected] Subject: Ames RPZ BFP During waterflow alarm testing on a Wet Pipe NFPA-13 System I witnessed a phenomena wherein the vane type waterflow switch fluctuated back in forth appx every 10 seconds making it impossible to set a 30 second retard. Supply Pressure is 60 psi static, 55 psi Residual at 2" Main Drain Test. The WF Switch is mounted horizontally in a straight length of 6" Sch 10 48" from closest change in direction. Inspectors test is located downstream end of a branch line 1/2" orifice in place. The sprinkler contractor suspects theres a problem with this particular BFP. Anyone had a similar problem. Thanks John Drucker Fire Protection Subcode Official (AHJ) New Jersey _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)