I have seen this several times before, but don't know the brand or model number of the BFP. The condition is aggravated by the presence of trapped air in the system, and sometimes occurs even if there is no BFP. You might try shutting the system down and relieving the pressure through the ITV. Then slowly fill the system with the ITV open until water comes out. This gets as much air out as is possible without providing other means of air release. Of course this won't help if the ITV is taken from the riser. [EMAIL PROTECTED] Ed Vining 4819 John Muir Rd Martinez CA 94553 925-228-8792
----- Original Message ---- From: John Drucker <[EMAIL PROTECTED]> To: [email protected] Sent: Monday, April 30, 2007 1:24:34 PM Subject: Ames RPZ BFP During waterflow alarm testing on a Wet Pipe NFPA-13 System I witnessed a phenomena wherein the vane type waterflow switch fluctuated back in forth appx every 10 seconds making it impossible to set a 30 second retard. Supply Pressure is 60 psi static, 55 psi Residual at 2" Main Drain Test. The WF Switch is mounted horizontally in a straight length of 6" Sch 10 48" from closest change in direction. Inspectors test is located downstream end of a branch line 1/2" orifice in place. The sprinkler contractor suspects theres a problem with this particular BFP. Anyone had a similar problem. Thanks John Drucker Fire Protection Subcode Official (AHJ) New Jersey _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)