I have seen this several times before, but don't know the brand or model number 
of the BFP.  The condition is aggravated by the presence of trapped air in the 
system, and sometimes occurs even if there is no BFP.
 
You might try shutting the system down and relieving the pressure through the 
ITV.  Then slowly fill the system with the ITV open until water comes out.  
This gets as much air out as is possible without providing other means of air 
release. Of course this won't help if the ITV is taken from the riser.
 
[EMAIL PROTECTED]
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792 



----- Original Message ----
From: John Drucker <[EMAIL PROTECTED]>
To: [email protected]
Sent: Monday, April 30, 2007 1:24:34 PM
Subject: Ames RPZ BFP


During waterflow alarm testing on a Wet Pipe NFPA-13 System I witnessed
a phenomena wherein the vane type waterflow switch fluctuated back in
forth appx every 10 seconds making it impossible to set a 30 second
retard. Supply Pressure is 60 psi static, 55 psi Residual at 2" Main
Drain Test.  The WF Switch is mounted horizontally in a straight length
of  6" Sch 10  48" from closest change in direction. Inspectors test is
located downstream end of a branch line 1/2" orifice in place.

The sprinkler contractor suspects theres a problem with this particular
BFP. Anyone had a similar problem.

Thanks

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to