I have witnessed the same problem. It was felt to be a combination of the
BFP and trapped air in the system. 

Craig Rauch, Certified Fire Safety Inspector
Washington Township Fire Department

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John Drucker
Sent: Monday, April 30, 2007 4:25 PM
To: [email protected]
Subject: Ames RPZ BFP


During waterflow alarm testing on a Wet Pipe NFPA-13 System I witnessed
a phenomena wherein the vane type waterflow switch fluctuated back in
forth appx every 10 seconds making it impossible to set a 30 second
retard. Supply Pressure is 60 psi static, 55 psi Residual at 2" Main
Drain Test.  The WF Switch is mounted horizontally in a straight length
of  6" Sch 10  48" from closest change in direction. Inspectors test is
located downstream end of a branch line 1/2" orifice in place.

The sprinkler contractor suspects theres a problem with this particular
BFP. Anyone had a similar problem.

Thanks

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey