The way I was taught was to keep the top valve open and the bottom valve
closed to collect the condensation in the drum.  Then, annually or as
needed, close the top valve and open the bottom valve to drain the
condensate. Then close the bottom valve and open the top valve to restore
it to a condensation collection condition.

NFPA 25 Table 5.1 requires this to be annually prior to freezing and as
needed.

Thank You

Rahe Loftin, P.E.
Region 7 - GSA
Office - 817-978-7299
Fax - 817-978-8644
Cell - 817-371-3102



                                                                           
                                                                           
             "Todd Williams -                                              
             work"                                                      To 
             <[EMAIL PROTECTED]>            [email protected]    
             Sent by:                                                   cc 
             sprinklerforum-bo                                             
             [EMAIL PROTECTED]                                     Subject 
             er.org                    drum drip                           
                                                                           
                                                                           
             05/13/2007 08:15                                              
             AM                                                            
                                                                           
                                                                           
             Please respond to                                             
             [EMAIL PROTECTED]                                             
              resprinkler.org                                              
                                                                           
                                                                           




When a drum drip is left in 'normal' position, which valves are open
and which closed? I always thought that the top valve is open and the
bottom valve shut. A fitter told me that both valves are supposed to
be shut. When I asked him where that came from, he admitted that's
what he was taught. Which is correct, if either?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to