Now that the water is clearing up on this one, let me muddy up again. I
agree that the drain does not need to be included in the hydraulic
calculations, however what happens to this configuration for a water
delivery calculation. I would think the tie-in would need to be included
because of the (minimal)added volume, but more so because the effect a
tie-in drain may have on the side of the system that is opposite your
calculated sprinklers and how it affects the compression of the air in other
areas of the system. I think this would definitely affect water delivery in
a low pressure system. 

I have done water delivery calculations, but I haven't attempted anything
other than side feed trees. In the calculations I have done, I have found it
amazing what some small things can affect a calculation where seconds are
precious. At this point, I don't not believe that the water delivery
software would accept this. And when I have some free time, I'll attempt it.
Does anybody have any thoughts on this one? I don't see anything in NFPA '13
'02 other than the delivery requirements.

Can of worms anyone?