Just going on memory here, but if it's the IBC and the open perimeter of
the basement is less than 50% of the total perimeter of the building,
then it isn't considered a story.  (As long as there is no fire truck
access). 

If I am wrong, I'm sure some one will call me out.

Any takers? 


Jamie Seidl


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - work
Sent: Tuesday, July 03, 2007 5:36 PM
To: [email protected]
Subject: 13R in wolfs clothing?

I am reviewing a set of plans for a 4 story plus partial basement motel.
The basement and first floor are designed per 13, the wood truss attic
is sprinklered, the sprinklers for the upper floors are fed from a
combination standpipe and the sprinklers on the floors are designed per
NFPA 13R. The contractor claims that the building is 13R and the areas
outside the dwelling units are protected per 13 in accordance with the
section of 13R. To me this doesn't sit well. 
There is 28000 sqft of "incidental" space (excluding 16000 sqft
attic) and 48000 sqft of residential. Does this really count as a 13R?
Is there (or should there be) some reasonable limits as to the amount of
space outside a dwelling unit before it is kicked up to the next level
of protection? I can't find anything in 13R that would not allow this
arrangement. The local building code gives no guidance. 
Any thoughts?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to