I am reviewing a set of plans for a 4 story plus partial basement motel. The basement and first floor are designed per 13, the wood truss attic is sprinklered, the sprinklers for the upper floors are fed from a combination standpipe and the sprinklers on the floors are designed per NFPA 13R. The contractor claims that the building is 13R and the areas outside the dwelling units are protected per 13 in accordance with the section of 13R. To me this doesn't sit well. There is 28000 sqft of "incidental" space (excluding 16000 sqft attic) and 48000 sqft of residential. Does this really count as a 13R? Is there (or should there be) some reasonable limits as to the amount of space outside a dwelling unit before it is kicked up to the next level of protection? I can't find anything in 13R that would not allow this arrangement. The local building code gives no guidance. Any thoughts?

Todd G. Williams, PE