Question:  What is the occupancy group?  If it's an R-1 motel, it
qualifies for 13R.

Presuming it's just a motel and doesn't have other uses, then the
auxiliary occupancies that are part of the motel operations (such as
housekeeping, lobbies, administration, etc.) are considered to be those
areas "outside of the dwelling units".   The attic doesn't require
protection under 13R, so its area is moot.

Unless there is some other public business within this building, it's
likely 13R.

Steve Leyton
PROTECTION DESIGN & CONSULTING


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - work
Sent: Tuesday, July 03, 2007 2:36 PM
To: [email protected]
Subject: 13R in wolfs clothing?

I am reviewing a set of plans for a 4 story plus partial basement 
motel. The basement and first floor are designed per 13, the wood 
truss attic is sprinklered, the sprinklers for the upper floors are 
fed from a combination standpipe and the sprinklers on the floors are 
designed per NFPA 13R. The contractor claims that the building is 13R 
and the areas outside the dwelling units are protected per 13 in 
accordance with the section of 13R. To me this doesn't sit well. 
There is 28000 sqft of "incidental" space (excluding 16000 sqft 
attic) and 48000 sqft of residential. Does this really count as a 
13R? Is there (or should there be) some reasonable limits as to the 
amount of space outside a dwelling unit before it is kicked up to the 
next level of protection? I can't find anything in 13R that would not 
allow this arrangement. The local building code gives no guidance. 
Any thoughts?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to