How about an end thought as the day winds down.

I spoke with the ICC about the RPBP vs DDC thing out of the IPC

Specifically section 608.  The funny part about this section is that it
speaks to a DDC throughout the section except when you have antifreeze or
foam in the system.  

The unique part is the commentary of the code.  The commentary (for you
sprinkler folks that's like the handbooks in ICC language) speaks very
specifically that if a non-potable water source is used in a fire truck then
a RPBP is required.  That is every single fire truck in the US.  If they
suck out of a pond, use hose to connect to a hydrant, use foam in a tank,
use any solvent or the like in the tank, etc. . . 

What is frustrating to me is that this language is very clear in the
commentary.  If that is what the "intent" truly is, then change the code
language to reflect the commentary.  I work for many municipalities and work
on the AHJ side and this is a tough issues.  

What is truly the probability of a Fire truck pumping into a FDC?
I think we all can agree that the RPBP is a maintenance nightmare.  If you
want I can summarize the commentary language on a future email.


Michael O'Brian
Code Savvy Consultants
www.codesavvyconsultants.com
313-618-6401
Fax 313-557-0294
 
************************************************
Take a look at www.inspector911.com the first site dedicated to code
enforcmenet (inspectors, fire marhsals, building officals, and plan
reviewers).  
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John Drucker
Sent: Friday, July 13, 2007 10:11 AM
To: [email protected]
Subject: RE: Backflow: Sprinkler System

Roland

Take a look at this;

2006 NSPC 10.5.9 - Exception (3) "Where fire protection include a fire
department connection, double check valve assemblies shall not be
permitted."

John
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Friday, July 13, 2007 10:04 AM
To: [email protected]
Subject: Re: Backflow: Sprinkler System

One of the aspects that drive an RPZ is when the fire dept draft from
non-potable sources (anytime).

Roland
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to