How about an end thought as the day winds down. I spoke with the ICC about the RPBP vs DDC thing out of the IPC
Specifically section 608. The funny part about this section is that it speaks to a DDC throughout the section except when you have antifreeze or foam in the system. The unique part is the commentary of the code. The commentary (for you sprinkler folks that's like the handbooks in ICC language) speaks very specifically that if a non-potable water source is used in a fire truck then a RPBP is required. That is every single fire truck in the US. If they suck out of a pond, use hose to connect to a hydrant, use foam in a tank, use any solvent or the like in the tank, etc. . . What is frustrating to me is that this language is very clear in the commentary. If that is what the "intent" truly is, then change the code language to reflect the commentary. I work for many municipalities and work on the AHJ side and this is a tough issues. What is truly the probability of a Fire truck pumping into a FDC? I think we all can agree that the RPBP is a maintenance nightmare. If you want I can summarize the commentary language on a future email. Michael O'Brian Code Savvy Consultants www.codesavvyconsultants.com 313-618-6401 Fax 313-557-0294 ************************************************ Take a look at www.inspector911.com the first site dedicated to code enforcmenet (inspectors, fire marhsals, building officals, and plan reviewers). -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Drucker Sent: Friday, July 13, 2007 10:11 AM To: [email protected] Subject: RE: Backflow: Sprinkler System Roland Take a look at this; 2006 NSPC 10.5.9 - Exception (3) "Where fire protection include a fire department connection, double check valve assemblies shall not be permitted." John -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Friday, July 13, 2007 10:04 AM To: [email protected] Subject: Re: Backflow: Sprinkler System One of the aspects that drive an RPZ is when the fire dept draft from non-potable sources (anytime). Roland _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)