Here is what the Illinois Plumbing Code says:

Section 890.1130  Protection of Potable Water

d) Fire Safety Systems. The installation of any fire safety system involving the potable water supply system shall be protected against backflow as follows:

1) Backflow protection is not required for fire safety systems constructed as follows:

A) The system shall be looped, with no dead ends, to allow circulation, to prevent the stagnation of water in the line;

B) The system shall not have any non-potable connections, or a fire department hose (Siamese) connection;

           C)        The system shall have 20 sprinkler heads or less; and

D) The system shall be constructed of potable water supply quality pipe in accordance with Appendix A: Table A of this Part.

2) A double detector check valve or double check valve backflow preventer assembly shall be installed at the fire safety system's point of connection to the potable water supply when a fire safety system has no chemical additives or non-potable connection, but has one or more fire department hose connections (for boosting pressure and flow to the fire safety system) that are served only by fire fighting apparatus connected to a public water supply or a fire department that does not use chemical additives or rely upon any non-potable water supply.

3) A fixed air gap with a break tank or other storage vessel or a reduced pressure principle backflow preventer assembly (RPZ) shall be installed at the fire safety system's point of connection to the potable water supply when:

A) The fire safety system contains additives such as antifreeze, fire retardant or other chemicals. (The RPZ may be located at the point of connection to that section of the system containing such additives when the system's connection to the water supply is protected by a double detector check valve backflow preventer assembly); or

B) Non-potable water flows into the fire safety system by gravity; or

C) There is a permanent or emergency connection whereby water can be pumped into the fire safety system from any other non-potable source; or

D) Fire department connections are available that could permit water to be pumped into the fire safety system from a non-potable source capable of serving the fire safety system. (A non-potable source of water shall be considered capable of serving the fire safety system under the following conditions: It must be capable of year-round use, maintained with at least 50,000 gallons of usable water not subject to freezing, accessible to fire fighting pumper equipment, and located within 1,700 feet of the facility.)

What we do is require a DDC unless it meets 3 A-D above, but we see RPZ's about 50% of the time without asking for it.

Jake
Land of Lincoln

John Drucker wrote:
Roland

Take a look at this;

2006 NSPC 10.5.9 - Exception (3) "Where fire protection include a fire
department connection, double check valve assemblies shall not be
permitted."

John


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Friday, July 13, 2007 10:04 AM
To: [email protected]
Subject: Re: Backflow: Sprinkler System

One of the aspects that drive an RPZ is when the fire dept draft from
non-potable sources (anytime).

Roland
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to