Aydin,

I've heard of a case where Galv. pipe was used for the sensing lines for the fire pump as you are referring to with disastrous results. The galv. flaking inside broke off and clogged the mercoid pressure switch thus preventing the pump from operating.

I would recommend you stick with the brass, copper or stainless steel as noted in the book.

Regards,

Gus Olson
GoCad, LLC

----- Original Message ----- From: "Aydın ÖZKAYA" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Saturday, July 14, 2007 1:53 PM
Subject: Why brass, copper or stainless steel, in Pressure Sensing Lines?


Dear All,

I wonder why, "brass, cooper or stainless steel" piping (but not galvanized
steel for instance) is specified for pressure sensing line for Fire Pump
Controls in NFPA 20  7-.5.2 & 9-5.2.

What is the rationality behind the "brass, copper or stainless steel"
limitation?

Thanks in advance...

Kind Rgds.

Aydın ÖZKAYA
KARİNA Design, Consultancy and Training Services Ltd.Co.
www.karina.gen.tr

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to