It's not just the ID of the sensing line piping, it's the potential to clog
the 3/32" orifi. You could use SS tubing with swagelock couplings if they're
easier to locate in an industrial construction setting- they're often used
for control and hydraulic lines for machinery, if copper is difficult to
find. 

glc 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gus Olson
Sent: Sunday, July 15, 2007 12:19 PM
To: [email protected]
Subject: Re: Why brass, copper or stainless steel, in Pressure Sensing
Lines?

Aydin,

I've heard of a case where Galv. pipe was used for the sensing lines for the

fire pump as you are referring to with disastrous results. The galv. flaking

inside broke off and clogged the mercoid pressure switch thus preventing the

pump from operating.

I would recommend you stick with the brass, copper or stainless steel as 
noted in the book.

Regards,

Gus Olson
GoCad, LLC

----- Original Message ----- 
From: "Aydın ÖZKAYA" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Saturday, July 14, 2007 1:53 PM
Subject: Why brass, copper or stainless steel, in Pressure Sensing Lines?


Dear All,

I wonder why, "brass, cooper or stainless steel" piping (but not galvanized
steel for instance) is specified for pressure sensing line for Fire Pump
Controls in NFPA 20  7-.5.2 & 9-5.2.

What is the rationality behind the "brass, copper or stainless steel"
limitation?