I like the specs for multiple FDC inlets, completely ignoring the
supplemental consideration of the FDC.

Current job- we install two 2,000 GPM pumps for high -density hi-tech system
requiring over 3000 GPM.The consultants wanted multiple storz to meet the
system demand via FD pumperS. Funny part- the local FD, 2 miles away, has a
1,000 GPM pumper and a 1,250 GPM pumper. Total, that's their fleet. By the
time additional apparatus (apparati?) arrive, there would be no sprinkler
pipe left at the roof to discharge thru if our pumps don't.

Washington DC is not the only place devoid of common sense.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jim Kettler
Sent: Monday, July 16, 2007 9:39 AM
To: [email protected]
Subject: RE: Backflow: Sprinkler System

With hope, all of those FDC's were used if there was an actual fire.
Generally speaking, standard FD operating procedures dictate that the first
arriving pumper support the sprinkler system via the FDC. If the fire is
already out, that much the better. If not, then the pumper will support the
system.

Personally, I am still struggling with why we (the fire service) began
asking for the FDC to be a large diameter hose connection, generally the 5"
stortz type. But that is another story.

James M. Kettler
Fire Marshal
Buckingham, PA




> Just how many FDC's get used in a fire? Almost every
> sprinkler saves that I
> read says the fire was out by the time the first responders
> got there, or
> the fire was controlled and only had to use a couple lines to
> put it out. I
> realize that high-rise fires on the left or right coast would
> be a different
> story. I've always wondered if the FDC was used and if so, why?
>
> David Autry
> Plans Examiner
> Nebraska State Fire Marshal's Office
> 246 S. 14th Street
> Lincoln, NE 68508
> 402-471-9659
> 402-471-3118 fax
> www.sfm.ne.gov


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to