Brian,

I have always found the appendix of the reference book "Hydraulic
Calculations of Automatic Sprinkler Systems" by Pat Brock to be a fantastic
and easy to use reference.  It has a full set of charts showing Hazen
friction loss values by pipe material, schedule, size, C-factor, etc.  I'm
sure there are other reference books with these charts as well.  

As Karen said, spreadsheets are great for this as well if you are not using
sprinkler design software.  However, I would be cautious when using plumbing
codes or other hydraulic reference charts to make sure they are based on the
Hazen Williams equation and not the Darcy-Weisbach friction loss equation,
which is more common in other industries.

Good luck,

Steve Kowkabany, P.E.
Fire Protection Engineer
Neptune Fire Protection Engineering LLC
216 Seagate Avenue Unit B
Neptune Beach, FL 32266
904-652-4200 Phone
904-212-0868 Fax

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Wednesday, July 25, 2007 3:35 PM
To: [email protected]
Subject: Friction Loss

What is the easiest way to figure friction loss when doing hydraulic calc's
by hand? I know the formula that's in the book but I was hoping there might
be a reference chart or something you could use instead. I have a
"Construction Master 5" calculator for working with feet and inches but it's
not set up to do compound formulas like the Hazen-Williams, sure would hate
to have to buy another one just to do formulas.......
 

 

 

 