Back in 1980+/- I was doing trees on an excel spreadsheet, a very simple
computerization of the old favorite hand calc sheet. One morning I received
back from ISO a bounced submittal of a 3rd floor addition to nursing home,
since there was an error in the calc. Same morning our fabricated pipe was
delivered. That afternoon Joe Manning was readying a Crowley calc program
for me, went there next day to get it "installed" and receive some training.

While the timing (release of fab before apvls) was really at fault, it was
time to invest in REAL software.
You get what you pay for in many instances.....save money in original
investment, spend more time in entry/troubleshooting/updating- not to
mention not being able to do grids.

I suppose, in parallel, there are contractors who limit their work to CPVC
since they don't have a couple 24" wrenches or a 300 machine to thread.
There is a cost to entering the business, and certainly it can be done at
various levels. 

Time warp- 1980 was pre-excel, it was in Supercalc 123 (pre DOS, for that
matter, CPM on an Osborne 28 lb "luggable" as laptops were known, 5" B&W
screen, twin 5.25" floppies, no hard drive, probably 2k RAM, looked like a
Singer sewing machine or small suitcase...)

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Thursday, July 26, 2007 11:49 AM
To: [email protected]
Subject: Re: Friction Loss

I like this idea. I made a simple Excel spreadsheet that does the
simplified  calc method from 13D. That method being so simple that it
probably takes more time to input the data into the spreadsheet than
to do it by hand but at least the computer doesn't make arithmetic
errors like I do. I suspect it wouldn't be too hard to develop a
matrix that produced a  multiplier either from a tabular base or by
doing a Hazen-Williams equation shouldn't be too hard. I suspect that
a lot of the commercial stand alone programs available are based on
Excel. But then again I'm not a computer guy so maybe I'm all wet.

On 7/26/07, Paul Sincaglia <[EMAIL PROTECTED]> wrote:
> Just a random thought in this regard.
>
> For years we have all been essentially stuck using either old hand calc
> methods (nothing wrong with them...just limited in what can be done
> easily/practically) or using one of the commercial software packages.
>
> Since the calculation principals (required input and output) are the same
> for all of us (NFPA 13 specific requirements), maybe it is time for
someone
> (NFPA, ASFA, NFSA, SFPE et al.) to sponsor the development of an "open
> source" hydraulics package that we can all use and improve as our
collective
> needs change.
>
> It is more than technically feasible today....and would certainly help the
> industry as a whole..save the current hydraulic software vendors.
>
> Just a thought.
>
> Paul
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Jimmy Waite
> Sent: Thursday, July 26, 2007 10:27 AM
> To: [email protected]
> Subject: RE: Friction Loss
>
> Brian,
> When I first learned to do calcs by hand I used a book by Robert Gagnon
> called "Design of Water-Based Fire Protection Systems."  It was a text
book
> for one of my college classes, but the back of the book contains friction
> loss tables for everything from steel, copper, Ductile Iron, PVC, and even
> cement lined.
>
> Jimmy Waite
> [EMAIL PROTECTED]
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
> Sent: Wednesday, July 25, 2007 1:35 PM
> To: [email protected]
> Subject: Friction Loss
>
> What is the easiest way to figure friction loss when doing hydraulic
calc's
> by hand? I know the formula that's in the book but I was hoping there
might
> be a reference chart or something you could use instead. I have a
> "Construction Master 5" calculator for working with feet and inches but
it's
> not set up to do compound formulas like the Hazen-Williams, sure would
hate
> to have to buy another one just to do formulas.......
>
>
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to