Brian, 
When I first learned to do calcs by hand I used a book by Robert Gagnon
called "Design of Water-Based Fire Protection Systems."  It was a text book
for one of my college classes, but the back of the book contains friction
loss tables for everything from steel, copper, Ductile Iron, PVC, and even
cement lined.  

Jimmy Waite
[EMAIL PROTECTED]


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Wednesday, July 25, 2007 1:35 PM
To: [email protected]
Subject: Friction Loss

What is the easiest way to figure friction loss when doing hydraulic calc's
by hand? I know the formula that's in the book but I was hoping there might
be a reference chart or something you could use instead. I have a
"Construction Master 5" calculator for working with feet and inches but it's
not set up to do compound formulas like the Hazen-Williams, sure would hate
to have to buy another one just to do formulas.......
 

 

 

 