Thanks George. I think that is what we will do. More time and money
wasted by our government.

Ron Fletcher 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Monday, July 30, 2007 2:02 PM
To: [email protected]
Subject: RE: Corps of Engineers Grv'd Cplg Spec

Ron-
If it helps, the word panel is SINGULAR, and does not necessarily
require one panel for each joint. Just that A PANEL be shown on the
drawings (marked "by others", if I were you) somewhere so that an access
to that space where the grooved couplings are installed. 

Obviously it could be impractical that someone could squeeze thru and
get to ALL couplings, but its also impractical that we could actually
fit spkr pipe in the "negative clearance" already existing in the space
where the 12" duct sits in a 10" space. So I'd show one PANEL and assume
their maintenance guy is as snake-like as the contractor that thinks
you're going to install accessss panels for him.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Monday, July 30, 2007 4:15 PM
To: [email protected]
Subject: RE: Corps of Engineers Grv'd Cplg Spec

"US Corps of Engineers Albuquerque District Specifications for Bureau of
Indian Affairs Kayenta Community School Replacement Navajo County,
Arizona"

Section 13930A.3.4.7 Pipe Joints: After referencing dial calipers,
go/no-go gauges, narrow-land micrometer, NFPA #13 and various other
filler material the make grooving of pipe sound difficult the section
finishes like this.

"Grooved joints shall not be used in concealed locations such as behind
walls or ceilings, unless an access panel is shown on the drawings for
servicing or adjusting the joint."

The RCP's do not show any access panels in the hard lids. I guess we
could show the panels on our drawings but then we would probably have to
provide them.

Thanks for your help.

Ron Fletcher
Aero Automatic
Phoenix, AZ

  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Monday, July 30, 2007 12:49 PM
To: [email protected]
Subject: Re: Corps of Engineers Grv'd Cplg Spec

Ron:

Which Gov. spec are you referring to?
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Fletcher, Ron" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, July 30, 2007 1:17 PM
Subject: Corps of Engineers Grv'd Cplg Spec


Anyone out there had any luck getting relief from a COE spec requiring
an access panel at every grooved coupling located in concealed locations
above hard lids or in walls?

Ron Fletcher
Aero Automatic
Phoenix, AZ
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to