If I'm reading 8.6.5.1.2 correctly, it says if you are against the wall- the soffit has to be 30" or under to be able to use this. Anything over 30" that is against the wall would require additional sprinklers. Or am I having another Monday today?
Bobby Gillett Project Manager [EMAIL PROTECTED] (731)-424-0130 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jay Stough Sent: Tuesday, September 18, 2007 10:43 AM To: AFSA SprinklerFORUM Subject: Sprinklers in Soffit? I have a school with classrooms that have a ceiling of 8'. there is a soffit along one wall that is 10" lower than the ceiling and 36" wide. I am drawing a blank as to whether I need sprinklers in the soffit. 8.6.4.1.1.3 says that if the difference in heights in the ceiling is less than 36", I can consider it a flat ceiling. 8.6.5.1.2 (3) limits the soffit to 30" in width. I can comply with table 8.6.5.1.2 and be less than 7'6 away from the wall. So can I eliminate sprinklers in the soffits? Joseph C. Stough SET, CFPS Tilley Fire Equipment Co. Tel. 215-345-8066 X22 Fax: 215-345-9357 [EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
