Joseph C. Stough SET, CFPS Tilley Fire Equipment Co. Tel. 215-345-8066 X22 Fax: 215-345-9357 [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Behalf Of Travis Mack Sent: Wednesday, September 19, 2007 1:47 PM To: [email protected] Subject: RE: Sprinklers in Soffit? No..I am saying that if you have a "soffit" that is 4" down from the ceiling, but is 36" off the wall, does that mean you are going to put a sprinkler in it? You need to comply with the beam rule, unless you have a soffit that meets the more lenient criteria of the "soffit rule." Assuming that you are 1/2" below the ceiling with the deflector, you could in theory have a soffit that is 4" below the ceiling and 5' off the wall and still not need a head in it. At least that is how I see it. Travis _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)