No..I am saying that if you have a "soffit" that is 4" down from the ceiling, but is 36" off the wall, does that mean you are going to put a sprinkler in it? You need to comply with the beam rule, unless you have a soffit that meets the more lenient criteria of the "soffit rule."
Assuming that you are 1/2" below the ceiling with the deflector, you could in theory have a soffit that is 4" below the ceiling and 5' off the wall and still not need a head in it. At least that is how I see it. Travis _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)