No..I am saying that if you have a "soffit" that is 4" down from the
ceiling, but is 36" off the wall, does that mean you are going to put a
sprinkler in it?  You need to comply with the beam rule, unless you have a
soffit that meets the more lenient criteria of the "soffit rule."  

Assuming that you are 1/2" below the ceiling with the deflector, you could
in theory have a soffit that is 4" below the ceiling and 5' off the wall and
still not need a head in it.

At least that is how I see it.

Travis