If the soffit is 10" down, assuming the deflector is 1/2" below the ceiling,
and using SSPs, then you need to be 3' from the edge of the soffit.  As long
as the soffit is not more than 4'6" off the wall, then you could make it at
7'-6" from the wall. Unless I am missing something!

T 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby Gillett
Sent: Wednesday, September 19, 2007 11:33 AM
To: [email protected]
Subject: RE: Sprinklers in Soffit?

Travis,

I agree, if your soffit is 4" down you can use table 8.6.5.1.2 and fig.
8.6.5.1.2 (a) and space off the wall correctly.
The original scenario is 10" down from the ceiling. It would be hard to keep
the spacing off of the wall without lowering the deflector greatly and/or
trying to use 9'-0 off of one wall.

Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack
Sent: Wednesday, September 19, 2007 12:47 PM
To: [email protected]
Subject: RE: Sprinklers in Soffit?

No..I am saying that if you have a "soffit" that is 4" down from the
ceiling, but is 36" off the wall, does that mean you are going to put a
sprinkler in it?  You need to comply with the beam rule, unless you have a
soffit that meets the more lenient criteria of the "soffit rule."  

Assuming that you are 1/2" below the ceiling with the deflector, you could
in theory have a soffit that is 4" below the ceiling and 5' off the wall and
still not need a head in it.

At least that is how I see it.

Travis

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ NOD32 2540 (20070919) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to