This is on a plan I am reviewing for a local AHJ. I questioned the
engineer/designer's layout (actually rejected it) in a review letter.
He has the test header being fed from a tee in the by-pass line
located downstream of the check valve but upstream of the last
control valve. I was uncomfortable with that arrangement. (There was
also no shut-off valve in the test header line).
At 12:43 PM 9/19/2007, you wrote:
Todd,
You're a PE that specializes in fire and if this forum is any
indication fire pumps seem to be a particular sub-specialty. What's
this other guy usually do?
On 9/19/07, FPDC <[EMAIL PROTECTED]> wrote:
> The diagrams in NFPA 20 show the connection for the test header prior
> to the valve on the discharge side of the pump. However, the diagrams
> are located in the appendix and I can't seem to find any text
> reference to it within the standard. Coul; someone enlighten me if
> the is any and if so, where? I've called for this and am being
> challenged by an engineer. Thanks
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)