Scott, Are you using EC sprinklers? Unless there are some newer listings that I am not aware of, there are no listed EC's for combustible obstructed construction. I am also assuming wood construction in this case, is it? Regardless, standard spray sprinklers would probably be a better choice in this situation since they only require a 6' separation. EC's do not sound like they would be an advantage for your situation anyway.
Bob Knight -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å... .... Sent: Monday, September 24, 2007 8:16 AM To: [email protected] Subject: 4:12 attic slope spacing between eave and peak There is a possible conflict between 2007 NFPA 13 8.6.4.1.4.3 and a manufacturers minimum separation distance rule. 8:12 > roof > 4:12 minimum separation of sprinklers is 8ft minimum distance from eave 5 ft along the eave. if we put one sprinkler at the peak and the downslope sprinklers > 5ft from the eave, I end up with sprinklers closer than 8 ft to the peak sprinkler. The slope is only long enough to take one sprinkler at the peak, and another along the slopes toward each eave. I am in favor of voiding the 8 ft manufacturer spacing, rather than setting a sprinkler down in the small apex of the eave. scot deal excelsior engineering _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.5.488 / Virus Database: 269.13.28/1023 - Release Date: 9/22/2007 1:27 PM No virus found in this outgoing message. Checked by AVG Free Edition. Version: 7.5.488 / Virus Database: 269.13.28/1023 - Release Date: 9/22/2007 1:27 PM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)