yep. i was. and, i go to the less than 8 ft separation across the slope (not down the slope) yes on EC yes on combustible obstructed
will go with less than 8 ft spacing against (not down the) slope to avoid the 20 psig end head pressure from 2007 Table 8.6.2.2.1(a). scot deal excelsior fire On 9/24/07, Bob Knight <[EMAIL PROTECTED]> wrote: > > Scott, > Are you using EC sprinklers? Unless there are some newer listings that I > am > not aware of, there are no listed EC's for combustible obstructed > construction. I am also assuming wood construction in this case, is it? > Regardless, standard spray sprinklers would probably be a better choice in > this situation since they only require a 6' separation. EC's do not sound > like they would be an advantage for your situation anyway. > > Bob Knight _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)