Hello å..., What EC head are you using listed for use with a 4:12 pitch roof ?
Monday, September 24, 2007, 10:16:28 AM, you wrote: > There is a possible conflict > between 2007 NFPA 13 8.6.4.1.4.3 > and a manufacturers minimum separation > distance rule. 8:12 >> roof > 4:12 > minimum separation of sprinklers is 8ft > minimum distance from eave 5 ft along the eave. > if we put one sprinkler at the peak and > the downslope sprinklers > 5ft from the eave, > I end up with sprinklers closer than 8 ft to the > peak sprinkler. The slope is only long enough > to take one sprinkler at the peak, and another > along the slopes toward each eave. > I am in favor of voiding the 8 ft manufacturer spacing, > rather than setting a sprinkler down in the small apex of the eave. > scot deal > excelsior engineering > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) -- Best regards, Charles mailto:[EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
