These are limited area systems that do not require waterflow alarm or FD
connection. The underground will require a 200 psi hydrostatic test. Is this
potable water supply?  Any approved material in NFPA 13.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, October 04, 2007 9:45 AM
To: [email protected]
Subject: RE: Underground Material

The site has a 12" CLDI firewater loop throughout supplied by a 120 psi
fire pump. The 2" would take connection to the 12" fire loop and run only
into the individual guardhouse. Inside the guardhouse will be a typical
riser assembly with a control valve, check valve, etc.



|---------+---------------------------------------->
|         |            <[EMAIL PROTECTED]>      |
|         |            Sent by:                    |
|         |            [EMAIL PROTECTED]|
|         |            prinkler.org                |
|         |            10/04/2007 09:40 AM         |
|         |            Please respond to           |
|         |            sprinklerforum              |
|---------+---------------------------------------->
 
>---------------------------------------------------------------------------
-----------------------------------------|
  |
|
  |
|
  |
To|
  |        <[email protected]>
|
  |
cc|
  |
|
  |
Subject|
  |        RE: Underground Material
|
  |
|
  |
|
  |
|
  |
|
  |
|
  |
|
 
>---------------------------------------------------------------------------
-----------------------------------------|




Are you planning on locating an alarm check valve within the guard shack
or just tagging these onto another existing system elsewhere?


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, October 04, 2007 9:24 AM
To: [email protected]
Subject: Underground Material

We have a situation where we need to put sprinklers in the guardhouses
at the entrances to a larger manufacturing facility. The one guardhouse
will have 6 heads and the other 4. We would like to supply the buildings
with 2"
underground. With the exception of copper what are my choices for an
approved 2" underground pipe material? The project is located in MA.

Matthew Drewello, PE

Fluor Corporation
100 Fluor Daniel Drive
Greenville, SC 29607
------------------------------------------------------------
The information transmitted is intended only for the person or entity to
which it is addressed and may contain proprietary, business-confidential
and/or privileged material.
If you are not the intended recipient of this message you are hereby
notified that any use, review, retransmission, dissemination,
distribution, reproduction or any action taken in reliance upon this
message is prohibited. If you received this in error, please contact the
sender and delete the material from any computer.

Any views expressed in this message are those of the individual sender
and may not necessarily reflect the views of the company.
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to