Isn't CPVC listed for underground?

Gary Stites
Operations Manager: Southern California
RLH Fire Protection
3430 Unicorn Road
Bakersfield, Ca. 93308
661-322-9344 #1343
Direct Line 661-410-1343
Direct FAX 866-871-2237
[EMAIL PROTECTED]
www.rlhfp.com

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike
Cabral
Sent: Thursday, October 04, 2007 9:07 AM
To: [email protected]
Subject: RE: Underground Material

PEX is rated at 160 psi working pressure @ 73 F & 130psi @ 120 F. There
is a 5 to1 safety factor at UL. . . in simplified terms pipe rated @ 175
psi must hold 875 psi for given amount of time. PEX pipe rated at 160
psi is tested at 800 psi. The product is suitable for the service.
--
Mike Cabral

---- George Church <[EMAIL PROTECTED]> wrote: 
> Wouldn't the pressure limitations of PEX be close to exceeded with a 
> 120 PSI pump?
> Obviously we don't know if that's BOOSTING A 50 psi static or 
> anything, but CPVC and PEX are both limited by temp/pressure ratings 
> less than conventional UG materials. Certainly, there are applications

> where both of these should work- although I've never used pex for 
> anything, can't offer any pros or cons..
> 
> Last week Mark and Ron from Aero discussed the high temps of UG water 
> in the desert installations they encounter (at the SprinklerForum 
> Reception), along with the residential seminar James gave mentioning 
> pressure/temp limitations of the two plastic materials mentioned.
> 
> Those who missed the AFSA Convention missed some great seminars, in 
> addition to the chance to see old and make new friends.
> 
> Oh, and there were a few booths in the Exhibit Hall :) where you can 
> talk to the factory reps (usually) about problems, such as the fastest

> acting PRV I needed for PLD inrush relief; spring-loaded is faster
than pilot-operated.
> 
> glc
> 
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Mike 
> Cabral
> Sent: Thursday, October 04, 2007 9:41 AM
> To: [email protected]
> Subject: Re: Underground Material
> 
> I don't want to appear self serving however, PEX is approved for 
> underground through 2" Here is a link to Rehau.
> 
> http://www.rehau-na.com/index.shtml
> --
> Mike Cabral
> the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to