How can you call it limited area if it's sprinklering the whole guard shack? It's just a small system. Backflow, shotgun and FDC (if over 20 heads, per our BOCA '93) If this is private work, use potable plastic. Separate loop? If it's public, and subject to public ahj's and state jurisdiction, 4" CLDI. And it's fitter's work here in MA if it's public. I've seen miles of ductile dug up and reinstalled by the local and that's not cheap. Tom Go Red Sox
These are limited area systems that do not require waterflow alarm or FD connection. The underground will require a 200 psi hydrostatic test. Is this potable water supply? Any approved material in NFPA 13. -----Original Message- The site has a 12" CLDI firewater loop throughout supplied by a 120 psi fire pump. The 2" would take connection to the 12" fire loop and run only into the individual guardhouse. Inside the guardhouse will be a typical riser assembly with a control valve, check valve, etc. Are you planning on locating an alarm check valve within the guard shack or just tagging these onto another existing system elsewhere? We have a situation where we need to put sprinklers in the guardhouses at the entrances to a larger manufacturing facility. The one guardhouse will have 6 heads and the other 4. We would like to supply the buildings with 2" underground. With the exception of copper what are my choices for an approved 2" underground pipe material? The project is located in MA. Matthew Drewello, PE _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)