Joe, I believe there's a difference between mesh shelving and mesh walls. The shelving is required to be a minimum of 18" or 36" below the sprinkler deflector and in reality will be much more than that. That distance allows the spray pattern to fully develop, and then the droplets are falling vertically through the mesh openings. A droplet that hits a solid portion of the mesh will still pass through in almost its original path. There ends up being no 'dry' areas below the mesh.
NFPA's minimum sprinkler-to-wall distance is 4". If a sprinkler were installed at that distance from a mesh wall (or slightly more), do you think a 30% obstructed mesh would disrupt the spray pattern development? I'm not so much thinking about the mesh nearest the sprinkler, but the mesh 30 degrees or so from perpendicular (if that makes sense). The spray pattern disruption wouldn't be that great, and that's probably why NFPA 13 allows mesh privacy curtains in light hazards to be ignored. I'd be a bit nervous ignoring them in ordinary or storage hazards. OK, tell me I'll all wet (or dry, depending which side of the mesh I'm on). Ed Kramer Littleton, CO >-----Original Message----- >From: [EMAIL PROTECTED] [mailto:sprinklerforum- >[EMAIL PROTECTED] On Behalf Of Joe Hankins >Sent: Monday, October 22, 2007 2:55 PM >To: [email protected] >Subject: Re: Vertical mesh wall > >I don't know that it is written anywhere for walls, but if rack shelves >can be considered open with wire mish shelving more than 70% open, the >same would go for walls. > >I was just responding to your statement that it was a grocery stock room >and was class IV. If they have specified how they want it done, why are >you worried about the wall? > >Joe > >Bobby Gillett wrote: >> Joe, >> >> Thanks for your reply as well. >> >> I was hoping that the 70% was accurate, but could only find it applied >in >> 8.6.5.2.2 as stated in an earlier response, which is for light hazard. >Is >> there somewhere else that states that this applies to something other >than >> LH? >> >> As far as the hazard classifications, this is an pre-engineered set of >> drawings that has us calc'ing two different ways in the same area. The >> design engineer firm wants these areas calc'd .45/2000 and .55 for the >most >> 4 demanding sprinklers. That is our instruction and other than the town, >> they are the AHJ along with the insurance company and they agree w/the >> design engineer for the project. We have no storage info other than how >to >> do it and they state in writing this is how they want it done. >> >> Bobby Gillett >> Project Manager >> [EMAIL PROTECTED] >> (731)-424-0130 >> >> -----Original Message----- >> From: [EMAIL PROTECTED] >> [mailto:[EMAIL PROTECTED] On Behalf Of Joe >Hankins >> Sent: Monday, October 22, 2007 3:33 PM >> To: [email protected] >> Subject: Re: Vertical mesh wall >> >> Bobby, >> >> If the "wall" is 70% open or more, it would not be an obstruction to >> sprinkler discharge. You would, however, have to extend the higher >> density beyond the "wall" because in terms of sprinkler operation, it >> would be absolutely no different than no wall. >> >> As an aside, there isn't a grocery store stock room anywhere in the real >> world that meets the criteria for a class IV commodity. Commodity >> classification is done on a pallet load/carton basis, not the overall >> mix in the room. If there are plastics or other higher hazard >> combustibles in the room, then it should be protected for that. If there >> is nothing worse than a class III, then that's your design. Unless it >> is filled with products having no more than 15% plastic in each carton >> or pallet load, it's not class IV. >> >> At some time of day and season of the year, any grocery store stock room >> is going to have lots of plastic or worse. You're not designing a >> sprinkler system to work some of the time. >> >> Joe >> >> Bobby Gillett wrote: >> >>> I guess my replies got lost, try again. >>> >>> >>> >>> This is Class IV comm and we have EC sprinklers (storage room in >>> Grocery/Shopping store). Wall of mesh keeps people out of a certain >areas >>> >> in >> >>> the back store room. >>> >>> >>> >>> >>> >>> Bobby Gillett >>> >>> Project Manager >>> >>> <mailto:[EMAIL PROTECTED]> >>> [EMAIL PROTECTED] >>> >>> (731)-424-0130 >>> >>> >>> >>> _______________________________________________ >>> Sprinklerforum mailing list >>> [email protected] >>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >>> >>> To Unsubscribe, send an email to:Sprinklerforum- >[EMAIL PROTECTED] >>> (Put the word unsubscribe in the subject field) >>> >>> >>> >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> To Unsubscribe, send an email to:Sprinklerforum- >[EMAIL PROTECTED] >> (Put the word unsubscribe in the subject field) >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> To Unsubscribe, send an email to:Sprinklerforum- >[EMAIL PROTECTED] >> (Put the word unsubscribe in the subject field) >> >> > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > >To Unsubscribe, send an email to:[EMAIL PROTECTED] >(Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)