Rich, Nothing from 13 should apply since it is both a life safety and property protection document. The presumption then is that 13D and 13R, being life safety only, have the property protection items from 13 removed. Personally I wouldn't be able to otherwise tell which rule was for which. Tyco's residential installation manual may be helpful although I don't believe the arrangement you describe is addressed. I will send this directly to you since I don't think we can send attachments through the forum.
On 10/29/07, Bob Knight <[EMAIL PROTECTED]> wrote: > Rich, > If this were my design I would not place a second sprinkler in a soffit that > is across the room and against the wall. The purpose of RES sprinklers in > part is to wet the walls, right? Draw yourself a side view elevation and > using common sense and good judgment, how much wall wetting will be > inhibited by the soffit. In my estimation, the amount would be negligible, > and therefore an additional sprinkler would not be necessary. In this > instance, the obstruction will not impede heat flow, nor have an appreciable > impact on discharge. If the obstruction were in the middle of the room the > story would be different since the pattern would be substantially impacted. > Letter of the law says yes, but the gray area using good judgment says no. > > Just my opinion based on nothing other then that, > > Bob Knight > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of R Richardson > Sent: Monday, October 29, 2007 11:41 AM > To: [email protected] > Subject: Residental Sidewall Soffit Obstruction > > Is the intent of NFPA 13 to treat a soffit on the opposite wall from which a > residential sprinkler head is installed as a beam with respect to > obstruction to spray pattern? Or can one ignore the area under the soffitt. > > The case we have is a 1 ft. deep soffit along the wall opposite from the > wall where the residential sidewall head is mounted. A straight NFPA 13 > application sends one to the beam rule, which requires the head to head to > be at least 14 ft. away, but it is only 10 ft. away. So does one really > have to install a head under the 1 x 1 ft. soffit on the opposite side of > the room where the sidewall head is located? > > Note: 2007 NFPA 13 section 8.7.5.1.5 for standard sidewall heads has an > allowance to ignore the soffit on the opposite wall, but this is the only > place we can find this situation addressed. > > Thanks, > > Rich Richardson > Seattle Fire Department > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > No virus found in this incoming message. > Checked by AVG Free Edition. > Version: 7.5.503 / Virus Database: 269.15.12/1097 - Release Date: 10/28/2007 > 1:58 PM > > > No virus found in this outgoing message. > Checked by AVG Free Edition. > Version: 7.5.503 / Virus Database: 269.15.12/1097 - Release Date: 10/28/2007 > 1:58 PM > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)