Rich,

Nothing from 13 should apply since it is both a life safety and
property protection document. The presumption then is that 13D and
13R, being life safety only, have the property protection items from
13 removed. Personally I wouldn't be able to otherwise tell which rule
was for which. Tyco's residential installation manual may be helpful
although I don't believe the arrangement you describe is addressed. I
will send this directly to you since I don't think we can send
attachments through the forum.

On 10/29/07, Bob Knight <[EMAIL PROTECTED]> wrote:
> Rich,
> If this were my design I would not place a second sprinkler in a soffit that
> is across the room and against the wall.  The purpose of RES sprinklers in
> part is to wet the walls, right?  Draw yourself a side view elevation and
> using common sense and good judgment, how much wall wetting will be
> inhibited by the soffit.  In my estimation, the amount would be negligible,
> and therefore an additional sprinkler would not be necessary.  In this
> instance, the obstruction will not impede heat flow, nor have an appreciable
> impact on discharge.  If the obstruction were in the middle of the room the
> story would be different since the pattern would be substantially impacted.
> Letter of the law says yes, but the gray area using good judgment says no.
>
> Just my opinion based on nothing other then that,
>
> Bob Knight
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of R Richardson
> Sent: Monday, October 29, 2007 11:41 AM
> To: [email protected]
> Subject: Residental Sidewall Soffit Obstruction
>
> Is the intent of NFPA 13 to treat a soffit on the opposite wall from which a
> residential sprinkler head is installed as a beam with respect to
> obstruction to spray pattern?  Or can one ignore the area under the soffitt.
>
> The case we have is a 1 ft. deep soffit along the wall opposite from the
> wall where the residential sidewall head is mounted.   A straight NFPA 13
> application sends one to the beam rule, which requires the head to head to
> be at least 14 ft. away, but it is only 10 ft. away.  So does one really
> have to install a head under the 1 x 1 ft. soffit on the opposite side of
> the room where the sidewall head is located?
>
> Note: 2007 NFPA 13 section 8.7.5.1.5  for standard sidewall heads has an
> allowance to ignore the soffit on the opposite wall, but this is the only
> place we can find this situation addressed.
>
> Thanks,
>
> Rich Richardson
> Seattle Fire Department
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> No virus found in this incoming message.
> Checked by AVG Free Edition.
> Version: 7.5.503 / Virus Database: 269.15.12/1097 - Release Date: 10/28/2007
> 1:58 PM
>
>
> No virus found in this outgoing message.
> Checked by AVG Free Edition.
> Version: 7.5.503 / Virus Database: 269.15.12/1097 - Release Date: 10/28/2007
> 1:58 PM
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to