Along with what Art said, I've been involved with projects were impellers
needed replaced and the RPM adjusted to meet the factory spec.  One that
comes to mind was just last year where a diesel pump was listed for 110 psi,
but was producing 240 psi at the 12th story roof level.  Just a tad too much
churn.  The supplying contractor came out and made his adjustments and all
has been fine since.

Bob Knight

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of art
Sent: Wednesday, October 31, 2007 8:01 AM
To: [email protected]
Subject: RE: Fire Pump performance as per the name plate

Gage readings during a pump test are not the final criteria. The pump speed
must be changed to pump rated speed and the pressure and flow is adjusted
accordingly. The new curve is to meet factory specs.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Wednesday, October 31, 2007 3:12 AM
To: [email protected]
Subject: RE: Fire Pump performance as per the name plate

I am aware of all that.

The 10% engine speed allowance is reflected in 20% pressure range. 

I get a pump package from a supplier. 

Is the name plate data means min. guarantied performance or is it
meaningless? 

Dan 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Frans Stoop
Sent: 30 October, 2007 3:33 PM
To: [email protected]
Subject: Re: Fire Pump performance as per the name plate

Dan,

NFPA 20-2007 paragraph 11.2.4.1.1:
"Engines shall be provided with a governor capable of regulating 
engine speed within a range of 10 percent between shutoff and maximum 
load condition of the pump."

Does this help: paragraph 11.2.4.1.2
"The governor shall be field adjustable and set and secured to 
maintain rated pump speed at maximum pump load." ?

The pump in concern should have a pressure relief valve installed per 
paragraph 5.18.1.1:
"Where a diesel engine fire pump is installed and where a total of 
121 percent of the net rated shutoff (churn) pressure plus the 
maximum static suction pressure, adjusted for elevation, exceeds the 
pressure for which the system components are rated, a pressure relief 
valve shall be installed."

If the water supply has its own storage tank(s), you may be able to 
solve the problem by piping the discharge side of this relief valve 
back to the water storage tank.

Although, note that paragraph 5.7.4.2 does not allow to use the 
relief valve for this purpose:
"Pressure relief valves shall not be used as a means to meet the 
requirements of 5.7.4.1."

You may also find other useful text in section 5.7.4* Maximum 
Pressure for Centrifugal Pumps.
like paragraph 5.7.4.1:
"The net pump shutoff (churn) pressure plus the maximum static 
suction pressure, adjusted for elevation, shall not exceed the 
pressure for which the system components are rated."

It says "net pressure" , no 5% allowance mentioned.

Frans Stoop
TOS architecture & fire protection
Netherlands


At 10:20 30-10-2007 +0200, you wrote:

>Dear All,
>
>I have got a problem with a fire pump.
>
>The pump performance does not match the name plant data.
>
>The cause is the Diesel Engine.
>
>The engine RPM deviation from "No Load" to 150% nominal is 90 rpm, just
over
>5% of the nominal (1760 rpm).
>
>The result is too high pressure (5% excess) at churning causing operation
of
>the 175psi relief valves of the sprinkler systems,
>
>At the other end, 150% flow, the pressure is 5% below the name plant data.
>
>The question: To what extent the pump supplier is bound by the name plant
>performance data.
>
>The supplier Rep. argues that 5% deviation is within the normal.
>
>
>Dan Arbel
>Tel: 972-4-8243337
>Fax: 972-4-8243278
>M: 972-52-2810593
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.503 / Virus Database: 269.15.13/1099 - Release Date: 10/30/2007
10:06 AM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.503 / Virus Database: 269.15.13/1099 - Release Date: 10/30/2007
10:06 AM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to