Along with what Art said, I've been involved with projects were impellers needed replaced and the RPM adjusted to meet the factory spec. One that comes to mind was just last year where a diesel pump was listed for 110 psi, but was producing 240 psi at the 12th story roof level. Just a tad too much churn. The supplying contractor came out and made his adjustments and all has been fine since.
Bob Knight -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of art Sent: Wednesday, October 31, 2007 8:01 AM To: [email protected] Subject: RE: Fire Pump performance as per the name plate Gage readings during a pump test are not the final criteria. The pump speed must be changed to pump rated speed and the pressure and flow is adjusted accordingly. The new curve is to meet factory specs. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of danarbel Sent: Wednesday, October 31, 2007 3:12 AM To: [email protected] Subject: RE: Fire Pump performance as per the name plate I am aware of all that. The 10% engine speed allowance is reflected in 20% pressure range. I get a pump package from a supplier. Is the name plate data means min. guarantied performance or is it meaningless? Dan -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Frans Stoop Sent: 30 October, 2007 3:33 PM To: [email protected] Subject: Re: Fire Pump performance as per the name plate Dan, NFPA 20-2007 paragraph 11.2.4.1.1: "Engines shall be provided with a governor capable of regulating engine speed within a range of 10 percent between shutoff and maximum load condition of the pump." Does this help: paragraph 11.2.4.1.2 "The governor shall be field adjustable and set and secured to maintain rated pump speed at maximum pump load." ? The pump in concern should have a pressure relief valve installed per paragraph 5.18.1.1: "Where a diesel engine fire pump is installed and where a total of 121 percent of the net rated shutoff (churn) pressure plus the maximum static suction pressure, adjusted for elevation, exceeds the pressure for which the system components are rated, a pressure relief valve shall be installed." If the water supply has its own storage tank(s), you may be able to solve the problem by piping the discharge side of this relief valve back to the water storage tank. Although, note that paragraph 5.7.4.2 does not allow to use the relief valve for this purpose: "Pressure relief valves shall not be used as a means to meet the requirements of 5.7.4.1." You may also find other useful text in section 5.7.4* Maximum Pressure for Centrifugal Pumps. like paragraph 5.7.4.1: "The net pump shutoff (churn) pressure plus the maximum static suction pressure, adjusted for elevation, shall not exceed the pressure for which the system components are rated." It says "net pressure" , no 5% allowance mentioned. Frans Stoop TOS architecture & fire protection Netherlands At 10:20 30-10-2007 +0200, you wrote: >Dear All, > >I have got a problem with a fire pump. > >The pump performance does not match the name plant data. > >The cause is the Diesel Engine. > >The engine RPM deviation from "No Load" to 150% nominal is 90 rpm, just over >5% of the nominal (1760 rpm). > >The result is too high pressure (5% excess) at churning causing operation of >the 175psi relief valves of the sprinkler systems, > >At the other end, 150% flow, the pressure is 5% below the name plant data. > >The question: To what extent the pump supplier is bound by the name plant >performance data. > >The supplier Rep. argues that 5% deviation is within the normal. > > >Dan Arbel >Tel: 972-4-8243337 >Fax: 972-4-8243278 >M: 972-52-2810593 > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > >To Unsubscribe, send an email to:[EMAIL PROTECTED] >(Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.5.503 / Virus Database: 269.15.13/1099 - Release Date: 10/30/2007 10:06 AM No virus found in this outgoing message. Checked by AVG Free Edition. Version: 7.5.503 / Virus Database: 269.15.13/1099 - Release Date: 10/30/2007 10:06 AM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)