Elevation? -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross Sent: Tuesday, October 30, 2007 6:22 AM To: [email protected] Subject: RE: Fire Pump performance as per the name plate
Is this a new pump? Under factory warrantee? To be accepted, it has to meet nameplate. If it didn't, why specify? New pump, you have a beef. Old pump, time to make some changes. Nameplate RPM is at 150%, not churn or design. Is rpm within the range of the driver? Sounds like someone needs a PRV. Tom Dear All, I have got a problem with a fire pump. The pump performance does not match the name plant data. The cause is the Diesel Engine. The engine RPM deviation from "No Load" to 150% nominal is 90 rpm, just over 5% of the nominal (1760 rpm). The result is too high pressure (5% excess) at churning causing operation of the 175psi relief valves of the sprinkler systems, At the other end, 150% flow, the pressure is 5% below the name plant data. The question: To what extent the pump supplier is bound by the name plant performance data. The supplier Rep. argues that 5% deviation is within the normal. Dan Arbel Tel: 972-4-8243337 Fax: 972-4-8243278 M: 972-52-2810593 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)