Ladies and Gents:

I've got a project in China where we have been instructed to use the 2006 
IBC, IFC etc.  For design and engineering purposes all disciplines per 
contract are to use the presumptuously named US International Codes 
series. 

However, there's always an exception isn't there. Because it's common in 
China, they want to use coated and wrapped carbon steel pipe for the 
underground.  Even when it was legal,  I never liked it because of the 
leakage potential, maintenance requirements, additional cathodic 
protection often required, etc.  NFPA 13 and 24, permit steel pipe only if 
specifically listed for underground service. 

I don't think I've ever seen listed underground steel pipe.   If any of 
you have, please advise.  Regardless of whether or not there is such an 
animal,  I may lose the battle since it won't likely be a case where a 
permit will be denied.

Thanks for your help.

Jim Roberts
------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to