In a light hazard situation, and the doors are self-closing, the contractor can assume only the design within the room - no sprinklers outside. They can then point to the owner and declare that the doors are not to be propped open.
On the other hand, if the engineer of record knows that self closing doors are not going to be closing, he can indicate that on the construction documents and forbid the use of the room design method unless the extra heads outside the room are calculated. If the contractor is effectively the engineer of record (design-build), then they can make the same determination - or not. I wonder why an owner would have self-closing doors AND keep them propped open? Seems a waste of money on door closers. Maybe the ME screwed up the HVAC design... Mark A. Sornsin, PE Fire Protection Engineer Ulteig Engineers, Inc. Fargo, ND 701.280.8591 [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Friday, December 21, 2007 9:14 AM To: [email protected] Subject: Room Design When you are performing an inspection of a system calculated using the room design approach, how do you handle all of the doors that are propped open? Or, how do you calculate these systems? Do you always go with the extra two sprinklers and assume the doors will be held open? Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146 410-544-3620 Phone 410-544-3032 FAX 412-400-6528 Cell _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)