While we are on this topic...We have a small debate in our office regarding the density/area method. Some say to ignore the walls completely through the entire calculation process, just like the example that NFPA 13 describes (which works great for a the typical warehouse with equal sprinkler spacing). Others say ignore the walls with regard to the general location of the remote area (1.2 rectangle) and then use the walls to determine the actual square footage of the remote area and to determine the actual gpm required from each sprinkler within the remote area. What do you all say?
Jason -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin Sent: Friday, December 21, 2007 8:35 AM To: [email protected] Subject: RE: Room Design I can't see a good reason for NFPA to nix the room design method - I've seen enough locations where the self-closing doors actually remain closed. But I can't see a contractor willingly avoid the room design either - not without potentially losing more work to the other guy. A classic example of why NFPA 13 is a minimum standard; and why (many times) there should be a third party taking responsibility for the design. Say, like an engineer of record for instance - one that knows what's going on, that is. Mark -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å... .... Sent: Friday, December 21, 2007 9:53 AM To: [email protected] Subject: Room Design propped open doors? propped open self-closing doors? that IS reality. that is why the Room Design method has to wake up and smell the coffee. not that the Room Design method is bad in intention. one, two, three sprinklers kabosh most LH/OH fires. just that there are some bad assumptions to the Room Design method. Like doors being closed. scot deal excelsior fire _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
