Let me explain a little further. It seems logical to locate the remote area (1.2 rectangle) without respect to the walls. Then fine tune the square footage of the remote area at the perimeter of that rectangle by taking the edge of the remote area to the nearest wall that gives you at least the 1.2 dimension of the rectangle. Imagine a typical office building without self closing doors. By a literal interpretation of code using the density/area method you would completely ignore the walls then perform the calcs as described in NFPA. Which would work fine if all of the sprinklers where centered in the room. One sprinkler may be 10'-0" from the adjacent sprinkler when ignoring the wall. And the same sprinkler 7'-6" off the wall when not ignoring the wall. Assume the spacing between this sprinkler and those in the other direction is 14'. Also, assume this is not a "small room". Ignoring the walls completely then the sprinkler gpm required is (10' x 14')0.10 = 14 gpm or (7 psi). Not ignoring the walls then the sprinkler gpm would be [(7.5' x 2)x14']0.10 = 21.0 gpm. If you use the 21.0 gpm as the sprinkler demand then logic follows that this same area to the wall can also be included as being part of the remote area inorder to satisfy the minimum area size. In essence you ignore the wall to get started only, then use the walls for the remainder of the calculation process. Does that help?
Jason -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Friday, December 21, 2007 1:29 PM To: [email protected] Subject: RE: Room Design I am not sure if I understand your question completely, but here is my attempt at an answer. The remote area is the actual physical area and not the hydraulic area. For example, consider a 22'x22' room with four sprinklers on 14' centers, the actual physical area is 484 sq. feet, but the hydraulic area is 784 square feet. Only 484 sq. ft. is in the design area. Have I interpreted your question properly? Paul J. Pinigis, P.E. Chief Life Safety Engineer -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jason Norton Sent: Friday, December 21, 2007 1:19 PM To: [email protected] Subject: RE: Room Design While we are on this topic...We have a small debate in our office regarding the density/area method. Some say to ignore the walls completely through the entire calculation process, just like the example that NFPA 13 describes (which works great for a the typical warehouse with equal sprinkler spacing). Others say ignore the walls with regard to the general location of the remote area (1.2 rectangle) and then use the walls to determine the actual square footage of the remote area and to determine the actual gpm required from each sprinkler within the remote area. What do you all say? Jason -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin Sent: Friday, December 21, 2007 8:35 AM To: [email protected] Subject: RE: Room Design I can't see a good reason for NFPA to nix the room design method - I've seen enough locations where the self-closing doors actually remain closed. But I can't see a contractor willingly avoid the room design either - not without potentially losing more work to the other guy. A classic example of why NFPA 13 is a minimum standard; and why (many times) there should be a third party taking responsibility for the design. Say, like an engineer of record for instance - one that knows what's going on, that is. Mark -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å... .... Sent: Friday, December 21, 2007 9:53 AM To: [email protected] Subject: Room Design propped open doors? propped open self-closing doors? that IS reality. that is why the Room Design method has to wake up and smell the coffee. not that the Room Design method is bad in intention. one, two, three sprinklers kabosh most LH/OH fires. just that there are some bad assumptions to the Room Design method. Like doors being closed. scot deal excelsior fire _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)