Let me explain a little further. It seems logical to locate the remote area 
(1.2 rectangle) without respect to the walls. Then fine tune the square footage 
of the remote area at the perimeter of that rectangle by taking the edge of the 
remote area to the nearest wall that gives you at least the 1.2 dimension of 
the rectangle. Imagine a typical office building without self closing doors. By 
a literal interpretation of code using the density/area method you would 
completely ignore the walls then perform the calcs as described in NFPA. Which 
would work fine if all of the sprinklers where centered in the room. One 
sprinkler may be 10'-0" from the adjacent sprinkler when ignoring the wall. And 
the same sprinkler 7'-6" off the wall when not ignoring the wall. Assume the 
spacing between this sprinkler and those in the other direction is 14'. Also, 
assume this is not a "small room". Ignoring the walls completely then the 
sprinkler gpm required is (10' x 14')0.10 = 14 gpm or (7 psi). Not ignoring the 
walls then the sprinkler gpm would be [(7.5' x 2)x14']0.10 = 21.0 gpm. If you 
use the 21.0 gpm as the sprinkler demand then logic follows that this same area 
to the wall can also be included as being part of the remote area inorder to 
satisfy the minimum area size. In essence you ignore the wall to get started 
only, then use the walls for the remainder of the calculation process. Does 
that help?

Jason 



 

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis
Sent: Friday, December 21, 2007 1:29 PM
To: [email protected]
Subject: RE: Room Design

I am not sure if I understand your question completely, but here is my attempt 
at an answer.  The remote area is the actual physical area and not the 
hydraulic area.  For example, consider a 22'x22' room with four sprinklers on 
14' centers, the actual physical area is 484 sq. feet, but the hydraulic area 
is 784 square feet.  Only 484 sq. ft. is in the design area.  

Have I interpreted your question properly?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jason Norton
Sent: Friday, December 21, 2007 1:19 PM
To: [email protected]
Subject: RE: Room Design

While we are on this topic...We have a small debate in our office regarding the 
density/area method.  Some say to ignore the walls completely through the 
entire calculation process, just like the example that NFPA 13 describes (which 
works great for a the typical warehouse with equal sprinkler spacing). Others 
say ignore the walls with regard to the general location of the remote area 
(1.2 rectangle) and then use the walls to determine the actual square footage 
of the remote area and to determine the actual gpm required from each sprinkler 
within the remote area. What do you all say? 

Jason

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin
Sent: Friday, December 21, 2007 8:35 AM
To: [email protected]
Subject: RE: Room Design

I can't see a good reason for NFPA to nix the room design method - I've seen 
enough locations where the self-closing doors actually remain closed. But I 
can't see a contractor willingly avoid the room design either - not without 
potentially losing more work to the other guy.

A classic example of why NFPA 13 is a minimum standard; and why (many times) 
there should be a third party taking responsibility for the design. Say, like 
an engineer of record for instance - one that knows what's going on, that is.

Mark 
 

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å... ....
Sent: Friday, December 21, 2007 9:53 AM
To: [email protected]
Subject: Room Design

propped open doors?
propped open self-closing doors?
that IS reality.

that is why the Room Design method
  has to wake up and smell the coffee.
not that the Room Design method is bad in intention.
  one, two,  three sprinklers kabosh most LH/OH fires.
just that there are some bad assumptions
  to the Room Design method.
  Like doors being closed.


scot deal
excelsior fire
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to