I am working on room that is approximately 25 x 25. The roof deck is
two layers of 3" thick tongue-and-grooved plank. Supporting this is a
series of 30" deep steel beams spaced 2'-9" O.C. This room is
presently unoccupied and will remain that way. (The space above was
contained a water tank. This is in a tower of an old mill). In my
pre-Christmas reading of the construction types, this seems to be an
anomaly. How do you address construction where the beam spacing is
less than 3 feet? Obstructed Construction only includes beams spaced
between 3 and 7.5 feet.
If you go to Chapter 8, assume obstructed construction and look at
the deflector distances, I would have to include a sprinkler in each
bay (since my beam depth exceeds 22"). I know I shouldn't be applying
logic to sprinklers, but 18 sprinklers to protect a 25 x 25
unoccupied room does seem to be overkill. Any thoughts? I think they
are way over budget on this project, so the idea of adding a ceiling
will be met with resistance. Any thoughts?
Merry Christmas to all
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut