I am working on room that is approximately 25 x 25. The roof deck is two layers of 3" thick tongue-and-grooved plank. Supporting this is a series of 30" deep steel beams spaced 2'-9" O.C. This room is presently unoccupied and will remain that way. (The space above was contained a water tank. This is in a tower of an old mill). In my pre-Christmas reading of the construction types, this seems to be an anomaly. How do you address construction where the beam spacing is less than 3 feet? Obstructed Construction only includes beams spaced between 3 and 7.5 feet.

If you go to Chapter 8, assume obstructed construction and look at the deflector distances, I would have to include a sprinkler in each bay (since my beam depth exceeds 22"). I know I shouldn't be applying logic to sprinklers, but 18 sprinklers to protect a 25 x 25 unoccupied room does seem to be overkill. Any thoughts? I think they are way over budget on this project, so the idea of adding a ceiling will be met with resistance. Any thoughts?

Merry Christmas to all

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________