I can't think of a good way to hold insulation at the top the beam. You might be able to do it with a spray on, but there is none on the job and the expense wouldn't be justified. I did a calculation and we couldn't even install a ceiling to get away from it because the volume of space between the two beams is 172 cuft, exceeding the 160 cuft in the concealed space section. Sounds like we're screwed.

At 12:00 PM 12/26/2007, you wrote:
bulls-eye

I guess one could simply use those bowed wire every couple of feet
(like one uses for insulation under the flooring in a house) but I
wouldn't be comfortable with that. What are you guys typically using
to reliable hold the insulation up?

Roland

On Dec 26, 2007, at 8:06 AM, Dewayne Martinez wrote:

Todd,
I think we talked somewhat about this in prior postings that the 22"
deflector distance couldn't be modified so one of the ideas was to
have
non-combustible insulation installed at the deck to make the deflector
to now within the 22" limit.  Now keeping the insulation up in the
pockets bring about another problem.
Dewayne

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Wednesday, December 26, 2007 9:56 AM
To: [email protected]
Subject: Re: construction type - extra heads

I have 30" deep beams spaced at 2'-9" o.c. If I space sprinklers in
every pocket, I have 18 sprinklers protecting a 625 sqft unoccupied
room. I was trying to look for a way out of it, since it does seem
excessive and will have a monstrous effect on the calcs. The space is
only accessible by a 2' x 2' hatch with a ladder, so bringing up
sheetrock to cover the ceiling is not practical. Looking for
thoughts or
ideas.


At 10:37 AM 12/26/2007, you wrote:
did you start with the definitions?  How can you call it anything but
obstructed?  I ASSUME the TC put the 3 to 7-1/2 ft since beam and
girders assemblies are TYPICALLY  spaced at a minimum but structural
loads are not always typical so neither are the beam placements.
Don't let the general description in the ANNEX get in the way of
defining ceiling type since it does NOT conflict with the base
definition.   Considering wood joists have the same impact on heat
flow and discharge, where's the beef?

The only time the minimum spacing will cause a REAL problem is
exceeding the 22 inch below the ceiling with concrete tees that are
less than 3 ft apart.  Twin tees are pretty common.

Roland

On Dec 24, 2007, at 5:38 AM, Todd Williams - FPDC wrote:

I am working on room that is approximately 25 x 25. The roof deck is
two layers of 3" thick tongue-and-grooved plank. Supporting this
is a
series of 30" deep steel beams spaced 2'-9" O.C. This room is
presently unoccupied and will remain that way. (The space above was
contained a water tank. This is in a tower of an old mill). In my
pre-Christmas reading of the construction types, this seems to be an
anomaly. How do you address construction where the beam spacing is
less than 3 feet? Obstructed Construction only includes beams spaced
between 3 and 7.5 feet.

If you go to Chapter 8, assume obstructed construction and look
at the

deflector distances, I would have to include a sprinkler in each bay
(since my beam depth exceeds 22"). I know I shouldn't be applying
logic to sprinklers, but 18 sprinklers to protect a 25 x
25 unoccupied room does seem to be overkill. Any thoughts? I think
they are way over budget on this project, so the idea of adding a
ceiling will be met with resistance. Any thoughts?

Merry Christmas to all

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED] (Put the word unsubscribe in the subject
field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to