Todd,
I think we talked somewhat about this in prior postings that the 22"
deflector distance couldn't be modified so one of the ideas was to have
non-combustible insulation installed at the deck to make the deflector
to now within the 22" limit.  Now keeping the insulation up in the
pockets bring about another problem.
Dewayne 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Wednesday, December 26, 2007 9:56 AM
To: [email protected]
Subject: Re: construction type - extra heads

I have 30" deep beams spaced at 2'-9" o.c. If I space sprinklers in
every pocket, I have 18 sprinklers protecting a 625 sqft unoccupied
room. I was trying to look for a way out of it, since it does seem
excessive and will have a monstrous effect on the calcs. The space is
only accessible by a 2' x 2' hatch with a ladder, so bringing up
sheetrock to cover the ceiling is not practical. Looking for thoughts or
ideas.


At 10:37 AM 12/26/2007, you wrote:
>did you start with the definitions?  How can you call it anything but 
>obstructed?  I ASSUME the TC put the 3 to 7-1/2 ft since beam and 
>girders assemblies are TYPICALLY  spaced at a minimum but structural 
>loads are not always typical so neither are the beam placements.
>Don't let the general description in the ANNEX get in the way of 
>defining ceiling type since it does NOT conflict with the base
>definition.   Considering wood joists have the same impact on heat
>flow and discharge, where's the beef?
>
>The only time the minimum spacing will cause a REAL problem is 
>exceeding the 22 inch below the ceiling with concrete tees that are 
>less than 3 ft apart.  Twin tees are pretty common.
>
>Roland
>
>On Dec 24, 2007, at 5:38 AM, Todd Williams - FPDC wrote:
>
>>I am working on room that is approximately 25 x 25. The roof deck is 
>>two layers of 3" thick tongue-and-grooved plank. Supporting this is a 
>>series of 30" deep steel beams spaced 2'-9" O.C. This room is 
>>presently unoccupied and will remain that way. (The space above was 
>>contained a water tank. This is in a tower of an old mill). In my 
>>pre-Christmas reading of the construction types, this seems to be an 
>>anomaly. How do you address construction where the beam spacing is 
>>less than 3 feet? Obstructed Construction only includes beams spaced 
>>between 3 and 7.5 feet.
>>
>>If you go to Chapter 8, assume obstructed construction and look at the

>>deflector distances, I would have to include a sprinkler in each bay 
>>(since my beam depth exceeds 22"). I know I shouldn't be applying 
>>logic to sprinklers, but 18 sprinklers to protect a 25 x
>>25 unoccupied room does seem to be overkill. Any thoughts? I think 
>>they are way over budget on this project, so the idea of adding a 
>>ceiling will be met with resistance. Any thoughts?
>>
>>Merry Christmas to all
>>
>>Todd G. Williams, PE
>>Fire Protection Design/Consulting
>>Stonington, Connecticut
>>www.fpdc.com
>>860.535.2080  _______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>To Unsubscribe, send an email to:Sprinklerforum- 
>>[EMAIL PROTECTED] (Put the word unsubscribe in the subject 
>>field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email 
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to