Todd, I think we talked somewhat about this in prior postings that the 22" deflector distance couldn't be modified so one of the ideas was to have non-combustible insulation installed at the deck to make the deflector to now within the 22" limit. Now keeping the insulation up in the pockets bring about another problem. Dewayne
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC Sent: Wednesday, December 26, 2007 9:56 AM To: [email protected] Subject: Re: construction type - extra heads I have 30" deep beams spaced at 2'-9" o.c. If I space sprinklers in every pocket, I have 18 sprinklers protecting a 625 sqft unoccupied room. I was trying to look for a way out of it, since it does seem excessive and will have a monstrous effect on the calcs. The space is only accessible by a 2' x 2' hatch with a ladder, so bringing up sheetrock to cover the ceiling is not practical. Looking for thoughts or ideas. At 10:37 AM 12/26/2007, you wrote: >did you start with the definitions? How can you call it anything but >obstructed? I ASSUME the TC put the 3 to 7-1/2 ft since beam and >girders assemblies are TYPICALLY spaced at a minimum but structural >loads are not always typical so neither are the beam placements. >Don't let the general description in the ANNEX get in the way of >defining ceiling type since it does NOT conflict with the base >definition. Considering wood joists have the same impact on heat >flow and discharge, where's the beef? > >The only time the minimum spacing will cause a REAL problem is >exceeding the 22 inch below the ceiling with concrete tees that are >less than 3 ft apart. Twin tees are pretty common. > >Roland > >On Dec 24, 2007, at 5:38 AM, Todd Williams - FPDC wrote: > >>I am working on room that is approximately 25 x 25. The roof deck is >>two layers of 3" thick tongue-and-grooved plank. Supporting this is a >>series of 30" deep steel beams spaced 2'-9" O.C. This room is >>presently unoccupied and will remain that way. (The space above was >>contained a water tank. This is in a tower of an old mill). In my >>pre-Christmas reading of the construction types, this seems to be an >>anomaly. How do you address construction where the beam spacing is >>less than 3 feet? Obstructed Construction only includes beams spaced >>between 3 and 7.5 feet. >> >>If you go to Chapter 8, assume obstructed construction and look at the >>deflector distances, I would have to include a sprinkler in each bay >>(since my beam depth exceeds 22"). I know I shouldn't be applying >>logic to sprinklers, but 18 sprinklers to protect a 25 x >>25 unoccupied room does seem to be overkill. Any thoughts? I think >>they are way over budget on this project, so the idea of adding a >>ceiling will be met with resistance. Any thoughts? >> >>Merry Christmas to all >> >>Todd G. Williams, PE >>Fire Protection Design/Consulting >>Stonington, Connecticut >>www.fpdc.com >>860.535.2080 _______________________________________________ >>Sprinklerforum mailing list >>[email protected] >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >>To Unsubscribe, send an email to:Sprinklerforum- >>[EMAIL PROTECTED] (Put the word unsubscribe in the subject >>field) > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > >To Unsubscribe, send an email >to:[EMAIL PROTECTED] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)